This old farmhouse has 'central heat' in the form of a freestanding 30k btu heater in the main room.

The heater was new in 1999 and I've put three replacement thermocouples in since then. Tonight it died again. I can't get it to sustain the pilot flame when I release the overrride no matter how long I held the override down.

The pilot flame seems vigorous and is aimed correctly to warm the thermocouple so I don't think that is the problem.

Is this likely a string of bad thermocouples, or is there something in the main valve that can go bad and then ignore the thermocouple? Have I reached the point where it is simpler to replace the entire heater?

Any comments will be very much appreciated.
 
   / Furnace thermocouple problem #2  
Sounds like a typical thermocouple situation to me. In my previous house I had a furnace with that kind of system and I had to replace the thermocouple every couple of years. Now I have electronic ignition so don't have that problem. Just keep a spare thermocouple on hand so that you can change it when needed.
 
   / Furnace thermocouple problem #3  
Thermo couples arent that expensive and pretty easy to change. Main thing is the shutoff valve closes when the thermocouple fails.

As for replacement of the heater that's a difficult question to even attemp to answer due to all the variables involved.

Egon
 
   / Furnace thermocouple problem #4  
A new heater is much more expensive than a few thermocouples. I use to be an HVAC servie tech/installer and one night I went to a house and found a bad thermocouple, when I went to my service truck I found that the other service man had got the only therm thermocouple long enough for this job off of my truck that morning. Rather than drive all the way back to the shop I took sandpaper and cleaned the snot out of the flame snesor and stuck it back in. Miraculously it worked but I knew it would only be a temp. fix, I showed the homeowner what I had done and since it was a mild night I told him I would bring a new one by the next day. The next day on the way home from work I gae it to him and he said he would put it on, I saw him a week later and he said he forgot to do it that night and it was still working. I asume you hae checked that the sensor is in the center of the flame and not the end.
 
   / Furnace thermocouple problem #5  
A few small things you might check, make sure the copper wire is not touching anything that would act as a heat sink. Check for corrosion on your thermocouple connection. Maybe you need to bend the mounting plate so the flame engulfs the sensor better. See if the gas jet for the pilot is partially plugged.
I always buy at least two spare thermocouples because when the furnace goes out it is most likely 2:00 am and below zero.
 
   / Furnace thermocouple problem #6  
ok this is a typical problem and one thing that EVRYONE has missed so far it the FURNACE GROUND! you HAVE to have a good ground to the unit or no matter how many NEW thermocouples you put on they will only work for a little while and quit... been there done that many times

like others said the thermocouple it's self usually will not go BAD persey, but they do carbon up and then they get changed (breaks off all the carbon) and it works again (it's mirical it was fixed HAD to have been a bad TC) ok anyhow use a bit of sand papoer to CLEAN off the junction of all the parts, and any rust , make sure there is a GOOD gorund wire running form the Furnace to the G in the home wire panel and then make sure the gas line is grounded as well. (Use a wire loope around the gas valve to catch BOTH sides of the piping and insulate the valve form acting as a ground path.

if these do not work, then you probably are getting a valve that is going south, there is small (~5 millie amp dc) signal reader inside which keeps the valve OPEN when the TC reads the flame, (flame generates the electrical current by heat/proxsimity to the TC and if the TC is not mounted correctly then it bleeds off the voltage, also DON"T KINK THEM, they center bi-metalic tube must not be kinked. it will break the insulation and the current will/can be lost through the mount and any metal that the external metal tube touches.) ok

HOPE THA HELPS

Martk M /forums/images/graemlins/smile.gif
 
   / Furnace thermocouple problem
  • Thread Starter
#7  
OK, I tried everything suggested above.

Except for the electrical stuff. This unit is too simple to have a millivolt thermostat, rather it's equivalent to an old water heater. The thermostat for the main burner is just a mechanical sensor tube hanging off the valve unit.

And... my problem is unrelated to the main burner thermostat. The problem is that the pilot flame won't stay lit when I let go of the override button.

It took several attempts, about 10 minutes total, to get the pilot flame to hold after installing the new thermocouple. This is the fourth thermocouple in four years. There's plenty of flame on it. As soon as I let go of the override button, the flame dies instantly but the thermocouple is so hot it continues to glow red/orange for a full 10 seconds before it cools down to dark and invisible in the burner chamber. I think it is sufficiently warmed.

A new aspect: I discovered a pair of wires coming from the thermocouple area of the valve and going to a sensor bolted onto the chimney just as it leaves the main burner chamber. I found the original installer's manual and the parts list hints that this is a cold-chimney sensor. So it looks like I need to override or replace this sensor as the next step in diagnosing why this thing is so hard to light.

Has someone with more experience than I replaced a cold-chimney sensor? Again, any advice?

Thanks!
 
   / Furnace thermocouple problem #8  
one other thing, there MAY be some carrosion built up down in the thermocouple mount to the valve, the small plunger looking thing has to contact a small plate down inside the valve this is where the milliamp current goes and this locks a small solinoid OPEN so the valve stays ON. the only other cause should/could be that the valve it;s self is starting to GO BAD, as in requiring more and more current to stay open.
I'm not familiar with teh cold chimminy switch. it is worth a try to see if it helps..

MarkM
 
   / Furnace thermocouple problem #9  
Are you on LP or natural gas. I am on LP and have similar problems every winter. I suspect in my case that there is a gas supply problem. Once the heater decides to stay lit, I don't have a problem until I turn it off for the season. I think that there may be a drop in supply pressure or an "air bubble" in the line.
 
   / Furnace thermocouple problem #10  
At this point, I suggest that you call a contractor that is experienced with repairing these things. I would hate to read about your home going bang in the middle of the night because of some malfunction. Natural and propane gas is not something that you want to mess with when there is a problem that is difficult to correct. If you bypass the wrong item, then it could possibly blow up with you in front of it. I know that we all think that we can fix almost anything ourselves, but this is one time that I believe that you should get a experience person in to look at it. If you mess up your car or tractor it only stops working. If you mess up the gas valve, your life is a risk, and your families also.... Just my unsolicited opinion from experience working with gas appliances. Mine blew up a few hours after I cleaned and reset the thermocouple and we had heat again. It was a defective gas valve that I didn't know about. It was on a recall for just this problem. Luck for us, the heater was an outside slab mounted unit. The only thing that was wrecked was the heater and some duct work...
 

Tractor & Equipment Auctions

2011 LONE STAR TRAILER GOOSENECK (A45046)
2011 LONE STAR...
2006 SHOP BUILT SINGLE AXLE 7-VALVE PUMP TRAILER (A45046)
2006 SHOP BUILT...
2024 Apex Hyperdisc T26 High Speed Tiller (A44789)
2024 Apex...
2013 Chevrolet Caprice Sedan (A42744)
2013 Chevrolet...
2014 MACK CXU613 (A45046)
2014 MACK CXU613...
2019 ALLMAND BROS, INC. LIGHT TOWER (A45046)
2019 ALLMAND BROS...
 
Top