TOMLESCOEQUIP
Platinum Member
I have a tempstar 80% furnace which has been acting up lately. it will cycle on , run the burner about 30 seconds or so then shut off............About a minute or 2 later is starts another sequence all over again but won't keep running. It's about 10 years old but hasn't given any problems till now and with Christmas just barely past, I'm not ready for a replacement expense just now ! Things I've checked already are: Flue vent not obstructed, forced power vent fan is working, sensor in plenum seems to turn fan on when unplugged and cuts flame off when I unplug it , sensor at front(toward me) on burner seems to work too............things shut down when I unhook it also. I have tried a jumper accross both sensors with no effect............It still shuts down after about 30 seconds no matter what. Also a small vaccumn diaphram off the power vent fan cage (connected by a tube) is working or seems to be. The brain module says honeywell continuous retry and that's what it's doing..........It acts like a flame sensor is not registering ignition but the main burner lights just fine............Any ideas would be really appreciated..........heating the house 30 seconds at a time is going to get old real fast............THANKS..............Tom