Building a fill station

   / Building a fill station #1  

LarryD

Veteran Member
Joined
Mar 23, 2004
Messages
1,165
Location
Whidbey Island, WA.
Tractor
TC33D
I need some ideas on converting this gravity feed day tank to a pumping tank for the tractor.

The original design filled the tank and floats shut the pump off when full. I can switch the hose around to draw from the tank (got to add a pick-up tube) and I have a 5/8 hose with fill nozzle to get the fuel in the tractor.

My big concern is the pump, since it was controlled with the relay and floats for start/stop, what is going to happen when I turn it on and its builds pressure before I start flow through the nozzle? My friend says, "just do it" but I'll probably use water if I do, the clean up will be WAY less troublesome.

My other option is to find a fill nozzle with a micro switch but so far that isn't producing any hits on the net. I could also find a pressure switch that would cut the pump off and tie that through the relay but without a foot valve on the pickup tube, I think the pump would just short cycle. Am I trying to make this pump do something it just isn't designed to do?

My other problem is finding a fuel filter that will fit under the pump cover. It has 8" of clear space but the fuel filter/water separators I see will need 10"+ of head space.

So help me build my own Rube Goldberg device and stay green by using as much of the original tank accessories as possible. The tank is 50gl and epoxy coated inside, so it's a good starting point.
 

Attachments

  • DSCN3495.JPG
    DSCN3495.JPG
    817.2 KB · Views: 421
  • DSCN3496.JPG
    DSCN3496.JPG
    918.1 KB · Views: 350
  • DSCN3497-1.JPG
    DSCN3497-1.JPG
    942.4 KB · Views: 366
  • Oberdorfer Pump.pdf
    141.6 KB · Views: 252
   / Building a fill station #2  
Larry is the electric motor on top centrifugal switch start motor. If so it puts out a pretty hefty spark on starting. Look inside while it is starting and you can see if it spark (arc). I don't know that this will be a problem, but please be careful.
 
   / Building a fill station
  • Thread Starter
#3  
I'm not familiar with the term "centrifugal switch" but if you mean power switch on and the pump is running then yes.

I was surprised to find the motor is not class 1 div. 1 but this unit has been pumping diesel fuel for more than 20 years without any problem so I feel comfortable with its new purpose. It was a day tank for an old 700kw Mitsubishi generator.

So today was spent plugging various ports on the tank and cleaning the inside. I got all the parts to make a pick-up tube so tomorrow I'll plumb the pump and do a test run on the new arrangement. I still have reservations on the pressure build-up on the pump but I'll be using water and a GFCI plug. It may all come down to replacing the pump in the cut-sheet with the one with the pressure relief valve or a different pump altogether. My goal is to get this up and running for less than $200...$50 spent today so I'm good.
 
   / Building a fill station #4  
We have a similar setup at work for our building generator. The 50 gallon day tank looks just like Larry's 1st pic. Its a standard type day tank unit with automatic fill used for standby generators. The 50 gallon day tank is in the same room as the generator and gets its fuel from an outside 1000 gallon tank when needed. On ours we plumbed in a manual 3 port valve (1 inlet, 2 outlets) so it either feeds the day tank automatically via the float operated switch or with a flip of the manual 3 port fuel valve it can be used to fill our portable 35 gal. fuel caddy with a flexible fuel hose. Our motor is a sealed motor and we added spin on fuel filters to both the in and out lines.
 
   / Building a fill station
  • Thread Starter
#5  
That's good information George.

Do you have any kind of control handle on the end of the flexible hose? If so, it sounds like there is not any problem with the pump developing pressure before you start to fill your portable tank. On the other hand, the pump model I have does not have the pressure relief valve and yours may be the "R" model. Any chance you could pull the cover off and look for that as depicted in the Oberdorfer cut-sheet I posted?
 
   / Building a fill station #6  
We use the on-off-auto switch and have ball valves since we also use it to feed another day tank for our building diesel fire pump. Our motor uses suction to pull fuel in from the outside tank then pushes it either in the day tank or to a valved setup on the wall. The day tank has a return line back to the 1K tank as well. The pump can be plumbed to pump from your day tank to your tractor. We use a flexible 3/4" clear hose with a quick coupler to fill the caddy tank. When I go in Monday I'll gather whatever info I can get off ours and let you know. I'll take my camera to get some pics as well. Should post back Monday afternoon. On a side note, we replaced our day tank about 6 years ago and told the company to haul away the old day tank. I didn't have a tractor or need for it then but wish I'd have taken it to use like you want to. And we don't have any control handle on the clear tube used to fill the fuel caddy. We just plug one end in the coupler, turn a couple valves and turn the pump switch to manual, when full we switch back to auto and return valves the way they were.
 
Last edited:
   / Building a fill station #7  
From the pump catalog page you provided.

"If the discharge line contains any throttling devices such as a shut-off valve,
a spray nozzle or other restrictive device, it is necessary to have a relief valve in the
system which returns the liquid to the suction side or to the tank."

You need to install a relief valve on the discharge. Don't run the pump with the discharge closed (fill nozzle off) even with water. You will either burst the hose, break the coupling, or break the pump.
 
   / Building a fill station
  • Thread Starter
#8  
You need to install a relief valve on the discharge. Don't run the pump with the discharge closed (fill nozzle off) even with water. You will either burst the hose, break the coupling, or break the pump.

Well team, todays test run produced mixed results.

I installed a pick-up tube on the tank port and was trying to figure out how to plumb the pump to the tube. The clearence was no more than 2" up and over so it was going to be difficult to span this with any sort of flexible tubing. As I was looking at the motor, it indicated a red wire on a certain terminal for CCW rotation, but the red wire was on a different terminal. Swap the red and black and the pump rotates the other way allowing me to use the original flex hose.

Time to test, open the fuel nozzle and turn the pump on. Works very well until I close the nozzle. The pump built pressure until the motor couldn't turn anymore...:eek:.

So now I'm going to install a pressure solenoid and wire it through the relay. Reading the literature leads me to think a 50psi solenoid will work nicely.

So now I need a solenoid and a filter/water separator. Grainger, can you hear me know?:D
 
   / Building a fill station #9  
I'm not familiar with the term "centrifugal switch" but if you mean power switch on and the pump is running then yes.

To further and better explain: Most electric motors of this size and single phase have two windings. Both are powered at starting and one is powered once the motor reaches a certain speed. One is turned off by a switch which opens up at this speed. The switch is opened by the centrifugal forces of the rotor speed. There is usually a spark created when it opens.
I hope this explanation helps. You can usually see the spark if you look in the end of the motor during starting.
 
   / Building a fill station #10  
Larry,
Sorry for the delay, I was tied up at work all day Monday and never got the chance to get info on our setup. We also have an Oberdorfer pump model N993 without relief (N993 has bigger inlet/outlet ports than your pump). Ours runs a 3/4" line in from the larger 1000 gal. tank through a 110V solenoid before the pump. We valved after the pump so we can direct the flow either to the day tank or out to a teed pipe system. (See Pics) We run an 1 1/2" return line back out to our 1K tank. Non of this info really helps with what you want to do but I can tell you we fill our fuel caddy 35 gal tank by turning the direction valve, opening the ball valve on the wall, plug the flex hose into the quick coupler, place hose in caddy and turn pump switch to run. It only take a few minutes to fill the caddy. When full, we reverse the procedure and put the pump switch back to auto position. Yours should be fairly simple to hook up with 110V power wired to your switch, suction side of pump connected to tank, discharge side of pump plumbed through a filter and finally to your flex hose. Valves may be added as needed.

In your case you'd leave the pump switch in the off position until your have your fuel hose in place between the pump and tank you're filling, open any valves you may have in line then turn on the pump until full.

With out a relief on ours we only risk pump or motor damage if we forget to open the proper valves. That happened one time when someone else tried to fill the caddy and did not have the quick coupler fully inserted and turned on the pump to fill the fuel caddy. The result was the pump and hose did not burst or blow a seal but since the pump could not turn (deadheaded) the motor burned up and I got called in to replace it. Maybe some of my pics will help you get yours plumbed up.

Pic 4 shows the quick coupler (left of green valve) we use to fill the fuel caddy. Yellow valve allows us to pump fuel up and into next room to keep the diesel fire pump day tank full. Pic 5 shows the fuel direction valve that switches flow from day tank to piping on back wall.

As long as you have your hand on the switch to turn off the pump when your tractor or portable fuel tank is full I don't think you'll need a relief. We've been running this setup the past eighteen years and and its only cost us one motor so far.
 

Attachments

  • Day Tank 4.JPG
    Day Tank 4.JPG
    77.6 KB · Views: 179
  • Day Tank 3.JPG
    Day Tank 3.JPG
    64.1 KB · Views: 206
  • Day Tank 2.JPG
    Day Tank 2.JPG
    64.7 KB · Views: 178
  • Day Tank 1.JPG
    Day Tank 1.JPG
    73.7 KB · Views: 229
  • Day Tank 5.JPG
    Day Tank 5.JPG
    74.5 KB · Views: 218
  • Day Tank 6.JPG
    Day Tank 6.JPG
    45.4 KB · Views: 177
   / Building a fill station
  • Thread Starter
#11  
That happened one time when someone else tried to fill the caddy and did not have the quick coupler fully inserted and turned on the pump to fill the fuel caddy. The result was the pump and hose did not burst or blow a seal but since the pump could not turn (deadheaded) the motor burned up and I got called in to replace it.

As long as you have your hand on the switch to turn off the pump when your tractor or portable fuel tank is full I don't think you'll need a relief. We've been running this setup the past eighteen years and and its only cost us one motor so far.

Thanks George,
That tank looks exactly like the Pryco tank I have. Must have come from the same factory.

I've got almost everything plumbed and the tank has been pressure washed inside. I don't want to rely on getting to the switch as a control means should something go wrong. I am going to the auto parts store tonight to look at fuel pressure switches. I figure I'll tee off the discharge side of the pump and wire that to the relay. It looks like I can get those in a pretty low pressure rating so it wont put an excessive load on the motor when fuel is not flowing.

Once I get the filter/water separator installed I'll post pictures of the whole thing. The CFO still shakes her head and mumbles comments like "boys and their toys" but this is way more fun that 5gl cans.:D
 
   / Building a fill station #12  
You could also use a remote start button and say a 12' cord with a momentary contact switch wired to the motor that would reach as far as your fill hose. Just hold the button to start your fill and let go to shut it off.

FYI, the original day tank we had looked just like yours. The one you see in my pics is basically the same tank but now due to EPA / DEC regulations has to have a built in spill container which you see at the bottom in pics 3 and 6. That is why we had to replace our day tank a few years back.
 
   / Building a fill station
  • Thread Starter
#14  
Actually Mr. Brown, my day job as a PM for an electrical contractor has me involved with another fuel storage/pumping project.

Talk about having a lifetime supply for the tractor.
 

Attachments

  • DSCN3504.JPG
    DSCN3504.JPG
    101.6 KB · Views: 145
  • DSCN3505.JPG
    DSCN3505.JPG
    127.7 KB · Views: 155
  • DSCN3501.JPG
    DSCN3501.JPG
    114.6 KB · Views: 138
   / Building a fill station #15  
Actually Mr. Brown, my day job as a PM for an electrical contractor has me involved with another fuel storage/pumping project.

Talk about having a lifetime supply for the tractor.

I must say this a bit more elaborate than what I need.
 
   / Building a fill station #16  
my biggest question on reverseing that setup.

is the pump a self priming suction pump.

if not your kinda SOL for getting it to suck fuel out of the tank instead of put fuel in the tank.

In George's setup at work its likely that the pump has fuel on the "back side" all the time so there really is no suction priming issues.

This is why most people use a sealed container and air hose to generate pressure on the inside to force the fuel out of the "suction" hose.

Personally i would forgo all the complicated electronic floats, motors etc and simply seal the metal can and add a chuck for an air hose and go that route. No pumps to maintain and no sparky sparky.
 
   / Building a fill station
  • Thread Starter
#17  
Steve,

It is a rotary gear pump and the literature says it can lift liquids 20'. Since I'm only lifting 30" it pumped the water pretty quickly. It does recommend a foot valve to help prevent the pump from running dry initialy but my test run had fluid moving within 10 seconds, I think that will be alright.

As for making this a pressure vessel, I don't believe its constructed to those kind of standards. It's fairly light, listed at 197lb. It also has 8" inspection plate (formerly held the floats) on top that I used to clean the tank out. It has a gasket but that also doesn't look like it would hold any pressure.

I've got my pressure switch so I'll start the final assembly. My other problem is the remaining water in the tank. It's got a drain but the current temps just are not letting it dry out. I think I'll lay it on its side and have a little heater I've got blow in some warmer air.
 
   / Building a fill station
  • Thread Starter
#19  
I can't take credit for my signature line since I saw it on a truck belonging to a general contractor I know...but I sure champion its message.
 
   / Building a fill station #20  
BobRip thanks for that explanation of the motor It was right to the point and understandable.Might I add That i learned about this type of motor when I used too large a pulley for my blower on one, It ran, but took awhile to do the switching part, which eventually urned into a smoke show, of cource the blower continued to flow the smoke through the house.
I sure cant fault the HF motor for this mistake. It clearly was mine.Apparently the pulley has to be sized so that the starter winding doesn't run long.
 

Tractor & Equipment Auctions

Caterpillar D5G LGP (A53317)
Caterpillar D5G...
Kubota M5-111 (A53317)
Kubota M5-111 (A53317)
2018 Chevrolet Impala Premier Sedan (A59231)
2018 Chevrolet...
SULLIVAN PATEK AIR COMPRESSOR (A58214)
SULLIVAN PATEK AIR...
Honda EM3500SX Portable Gasoline Generator (A59228)
Honda EM3500SX...
Caterpillar 906M (A53317)
Caterpillar 906M...
 
Top