I will try to explain this clearly but feel free to ask for further info if needed.
By brother-in-law lives in a Mobile Home with metal exterior. He has been living in this home for several years without any problems. The home has a four-wire connection (2 hots, common, ground) coming from a pole just outside the house (about 45' wire run counting the down the pole, under the ground and up into the panel - all in PVC conduit). It has been hooked up this way since the house was connected and there have been no changes to the setup.
Now, there is a problem. If you are standing on the ground (either bare-foot or in shoes that will conduct) and touch the metal skin of the house you will get shocked. The same goes for the panel box on the pole. When measured with one probe stuck into the ground and the other probe touching the MH skin or the panel box, it will read somewhere between 55 and 96 volts.
The panel box on the pole has a main, a 100 amp breaker for the MH, a breaker for the pump and a breaker that goes to a sub-panel in an out building.
Turning off the breaker to the pump has no effect on the "leaking" power. Turning off the breaker to the sub-panel has no effect on the "leaking" power.
However, turning off the breaker to the MH kills the power going to the panel box and the MH skin - the "leaking power" stops.
Further testing has shown that if I disconnect the green ground wire from the MH panel, the "leaking power" also stops.
I should mention that when looking for the problem, I did find that the White Common from the meter pan to the main panel on the pole was lose and burned at the meter connection. This has been fixed. However, the "leaking power" still persists.
Any thoughts or suggestions will be greatly appreciated.
By brother-in-law lives in a Mobile Home with metal exterior. He has been living in this home for several years without any problems. The home has a four-wire connection (2 hots, common, ground) coming from a pole just outside the house (about 45' wire run counting the down the pole, under the ground and up into the panel - all in PVC conduit). It has been hooked up this way since the house was connected and there have been no changes to the setup.
Now, there is a problem. If you are standing on the ground (either bare-foot or in shoes that will conduct) and touch the metal skin of the house you will get shocked. The same goes for the panel box on the pole. When measured with one probe stuck into the ground and the other probe touching the MH skin or the panel box, it will read somewhere between 55 and 96 volts.
The panel box on the pole has a main, a 100 amp breaker for the MH, a breaker for the pump and a breaker that goes to a sub-panel in an out building.
Turning off the breaker to the pump has no effect on the "leaking" power. Turning off the breaker to the sub-panel has no effect on the "leaking" power.
However, turning off the breaker to the MH kills the power going to the panel box and the MH skin - the "leaking power" stops.
Further testing has shown that if I disconnect the green ground wire from the MH panel, the "leaking power" also stops.
I should mention that when looking for the problem, I did find that the White Common from the meter pan to the main panel on the pole was lose and burned at the meter connection. This has been fixed. However, the "leaking power" still persists.
Any thoughts or suggestions will be greatly appreciated.