you’re likely fine at 50A, but do note that AWG-6 copper will see temp rise near 60C at 75A, which could put your insulation at 100C on a hot day, and likely violates the breaker’s max terminal temperature. Check insulation and breaker temperature ratings, insulation is probably no higher than 90C and most breakers are lower than that, and consider a smaller breaker for slow-blow component. You could keep a series fast-blow much higher, if you want.I ran a duplex 6awg wire to the back and the 3rd function connections with 50amp Anderson power poles, both tied to the same 75amp breaker by the battery.
Lets me plug in a little winch on the loader or run my sprayer on the back.
The good news is that running hot terminal on breaker will lower its thermal trip rating, so at least a little bit fail safe.